As above you should not over rate a fuse, Fitting a higher rated fuse can be dangerous as it allows a fault to heat up.
A fuse(s) is needed in any electrical system (AC or DC). These protection devices react to the amount of heat being produced by electricity passing through wires and/or components. They are used so as to protect wires and components from the extreme heat produced should there be an electrical overload or short circuit.
When a short or overload occurs, the amps being drawn spike and this increases the heat produced in the wiring and components. When this occurs, a fuse or circuit breaker reacts almost instantly to stop the flow of electricity in the circuit and thereby stopping heat production.
You should never exceed the fuse rating advised by the manufacturer. For a fuse to open in a fault condition almost instantly (a few hundred milliseconds ) it can require current of 2.2 to 3 times the rating of the fuse. For our controllers we recommend 7.5 amp fuses so the actual current to open the fuse may be as high as 22.5 amps over rating the fuse is dangerous. (Check the manufacturers instructions for correct rating)
In very rare cases if current is only slightly above or close to the rating of the fuse for prolonged periods there is not sufficient heat or current to blow the fuse, in this case the heat can build up and cause the fuse to melt.
For example a 15 amp fuse will happily supply current up to 15 amps but will not blow. (to blow it could require current of up to 45 amps) The fuse will however gradually get hot over time in testing at Spring I have seen a 7.5 amp fuse heat to 62C and not blow
Without PROPERLY-SIZED FUSES, this quick break in the circuit would not be possible, and damage to components and even FIRE could result.
If you are having a problem with fuses "blowing" please know that these devices are doing their job! It is important that you NOT replace a fuse or breaker with a higher-rated one. Check the circuit for shorts or overloads.
Damaged, rusted or worn connectors
Damaged cable
Bare cables touching each other or to metal panels
Poor connection (example would be insulation not stripped back)