can anyone send me a diagram of the pipework for a 400gpd RO. I have just changed it and cannot get TDS below 530 on either waste or product water. I must have done something wrong. Any other suggestions of what could be wrong would be helpful too
Cheers
AJ
-
HAVE YOU REMEMBERD THAT THE FIRST 5 GALLONS
IS WASTE. THE NEW MEMBRANES ARE COATED WITH
SOMETHING TO PRESERVE THEM.
CHEERS JEFF.
-
i allways find the first 12 hours of production is poor quality